Help with Lighting Position and Voltage Drop
Discussion in 'Ask the Landscape Lighting Experts' started by EBelew, Oct 25, 2023.
  1. EBelew
    EBelew New Member
    Is this possible? Or is there to much distance between H1 and H2? Taking H2 back to the transformer would be approximately a 65ft run with the 14ga wire furnished.
  2. Robert Mason
    Robert Mason Active Member
    EBelew: When Evan was still posting in this forum, he advised against connecting hubs in series. He would have recommended separate main lines to each hub. With that in mind, on page 9 of the downloadable installation guide for the 300W transformer is an equation for calculating voltage drop. My quick calculation for a 65 foot run with 14 gauge cable suggests a modest 1.1 voltage drop to the hub, with an additional drop for each fixtures cable length and gauge. So long as you stay above something around 10 volts at each fixture, a 65 foot run should work fine. If your 100 watt Slim Line transformer has only 15 volt outputs, staying above 10 is not an issue. Two mainlines will work just fine. Bob Mason
    EBelew likes this.
  3. EBelew
    EBelew New Member
    Thanks. I appreciate it. I'll give it a try.
  4. EBelew
    EBelew New Member
    Thank you for the help
  5. Robert Mason
    EBelew: Saw your other photo also. Well done. And you're welcome. Bob
    EBelew likes this.